Ask Experts Questions for FREE Help !
Ask
    cmedvec123's Avatar
    cmedvec123 Posts: 14, Reputation: 2
    New Member
     
    #1

    Jan 5, 2008, 03:41 PM
    Gas valve cross reference
    I have an heil warm air furnace,with a smartvalve gas valve.sv9500n2674... can't find exact number gas valve.only one I found was an sv9501m2813 says replaces all sv9500 valves.can anybody verify this is true.new in the hvac field not too sure.this natural gas unit,not lp.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Jan 5, 2008, 05:54 PM
    Propane or natural gas?

    This is a Honeywell 2 stage valve I believe.

    Honeywell

    http://customer.honeywell.com/techli...0s/69-1238.pdf
    tsa7man's Avatar
    tsa7man Posts: 154, Reputation: 9
    Junior Member
     
    #3

    Jan 5, 2008, 08:25 PM
    If you are talking about a natural gas furnace, the Honeywell SV9500 ( single stage gas valve) was replaced by a SV9501 gas valve ( both single stage ) Be sure to set the proper manifold gas pressure with a manometer as per the ID label specs, which should be 3.5 inches of WC... so you don't over fire the unit !
    cmedvec123's Avatar
    cmedvec123 Posts: 14, Reputation: 2
    New Member
     
    #4

    Jan 5, 2008, 10:49 PM
    Quote Originally Posted by tsa7man
    If you are talking about a natural gas furnace, the Honeywell SV9500 ( single stage gas valve) was replaced by a SV9501 gas valve ( both single stage ) Be sure to set the proper manifold gas pressure with a manometer as per the ID label specs, which should be 3.5 inches of WC..... so you don't over fire the unit !
    Yah but on honeywell web site it says the sv9501 is slow opening valve is that the same as 2 stage.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #5

    Jan 6, 2008, 12:21 AM
    Every once in a while a manufacturer will request Honeywell or white Rodgers to make a special valve for them. It is possible you have one of those. I would call a Heil HVAC contractor and see if they can fix you up with the same valve you have.
    tsa7man's Avatar
    tsa7man Posts: 154, Reputation: 9
    Junior Member
     
    #6

    Jan 6, 2008, 05:33 PM
    Post the full model number and serial number of your Heil furnace, And I'll tell you want is the correct gas valve for that unit... as per ICP ( Heil's) parts program...
    cmedvec123's Avatar
    cmedvec123 Posts: 14, Reputation: 2
    New Member
     
    #7

    Jan 6, 2008, 06:39 PM
    Quote Originally Posted by tsa7man
    Post the full model number and serial number of your Heil furnace, And I'll tell you want is the correct gas valve for that unit...as per ICP ( Heil's) parts program....
    the unit is a heil,model #NUGM075EGB1,SERIAL #L953217763... GAS VALVE THAT IS IN UNIT IS SV9500N2674.
    tsa7man's Avatar
    tsa7man Posts: 154, Reputation: 9
    Junior Member
     
    #8

    Jan 7, 2008, 05:12 AM
    The original gas valve is a SV9500M which has the following ICP /Heil part numbers... 1009093,. Their parts program also lists the SV9501M which has the following part numbers... 1096725, and 1170430. These are all single stage gas valves for natural gas. The SV9501 is an up-grade from the earlier SV9500 series. Be sure to set your gas pressure for the manifold side at 3.5 inches of WC for natural gas if that is your gas supply. If NOT, the gas valve has to be converted to run LP / propane gas
    cmedvec123's Avatar
    cmedvec123 Posts: 14, Reputation: 2
    New Member
     
    #9

    Jan 7, 2008, 05:11 PM
    Quote Originally Posted by tsa7man
    The original gas valve is a SV9500M which has the following ICP /Heil part numbers....1009093, ...Their parts program also lists the SV9501M which has the following part numbers... 1096725, and 1170430. These are all single stage gas valves for natural gas. The SV9501 is an up-grade from the earlier SV9500 series. Be sure to set your gas pressure for the manifold side at 3.5 inches of WC for natural gas if that is your gas supply. If NOT, the gas valve has to be converted to run LP / propane gas
    ... thanx for all the help,installed sv9501 gas valve all ops. OK now thanks again...
    draisland7's Avatar
    draisland7 Posts: 1, Reputation: 1
    New Member
     
    #10

    Jan 19, 2010, 06:45 PM

    Nat gas-Lo 1"-4"w.c. Hi 2"-5" w.c.
    LP- Lo 4.5"-10"w.c Hi- 8"-12" w.c
    For 2 stage valves

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Filter cross reference [ 6 Answers ]

I have a 1990 Nissan Terrano 2.7l diesel. It was imported from Japan. I am looking for replacement filters (oil, fuel, air) and cannot find a cross-reference list for North American parts. Does anyone know of either a forum where this might be found or someone / place that could tell me the North...

ATV oil filter cross reference [ 3 Answers ]

I am looking for a cross reference for oil/air filters for ATV's. I have 2 ATV's and am getting tired of being ripped off for filters. Yamaha Grizzly 660 2005 Kawasaki Praire 350 2006 Any help would be appreciated. Thanks.

Reference list [ 2 Answers ]

Hi guys.. I need some help here in writing a references list for a paper I'm writing now... I took data from the following resources and I dono the scientific way in writing them to my reference list : 1- a TV or Radio speech 2- a paper that was discussed in a conference 3- an interview ...


View more questions Search