    jonwilliam's Avatar
    jonwilliam Posts: 31, Reputation: 1
    Junior Member
     
    #1

    Feb 8, 2009, 07:27 AM
    To replace A Cam Stat Fan limit with a Honeywell
    Hi guys,
    Am going to replace the current Cam Stat Fan limit on my old furnace coleman with a honey well 8 ". Could you specify the diagram for wiring on honeywell.
    Thanks for your prompt answers
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Feb 8, 2009, 07:37 AM
    It depends upon the cam stat. Some are special and you cannot use a Honeywell to replace it with.

    Post Exact model of the Cam Stat and post the exact model of the Honeywell.

    I will see if I can find the wiring diagrams for the cam stat to see if it will work.

    NOTE many furnace manufactures require the cam stat style for the blower and limit control section to work properly. Just a warning.
    jonwilliam's Avatar
    jonwilliam Posts: 31, Reputation: 1
    Junior Member
     
    #3

    Feb 8, 2009, 09:07 AM
    Quote Originally Posted by hvac1000 View Post
    It depends upon the cam stat. Some are special and you cannot use a Honeywell to replace it with.

    Post Exact model of the Cam Stat and post the exact model of the Honeywell.

    I will see if I can find the wiring diagrams for the cam stat to see if it will work.

    NOTE many furnace manufactures require the cam stat style for the blower and limit control section to work properly. Just a warning.
    Hi HVAC 1000Thanks so much for your prompt answer

    Here are the model no for Cam Stat FALTS F7C-05T-120.A and on two terminals you can see 24VAC HTR which is going to be replaced with Honeywell L4064B, L,R & W
    Would appreciate a wiring diagram pictorial or schematic whatever and thanks again chow
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #4

    Feb 8, 2009, 09:17 AM
    Follow wiring diagram below link.
    Attached Images
  1. File Type: pdf 8173000400.pdf (64.7 KB, 824 views)
  2. hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #5

    Feb 8, 2009, 09:18 AM
    Here is your new one

    http://customer.honeywell.com/techli...0s/69-0117.pdf
    jonwilliam's Avatar
    jonwilliam Posts: 31, Reputation: 1
    Junior Member
     
    #6

    Feb 8, 2009, 10:08 AM
    Quote Originally Posted by hvac1000 View Post
    Hvac 1000 thanks again
    Then what about the two wires 24vac which terminals do they sit on the honeywell please and thks . Well the other four terminals can be figured out though. My guessestimate is that those two wires 24vac can sit on the two terminals in the middle of honeywell fan limit as heat strip am i right??
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #7

    Feb 8, 2009, 10:29 AM
    The reason I left this up to you was the wiring is VERY critical if you have a mix of 24 volt and 120 volt wiring in use on your furnace. I have no idea what you have but if you do have a low and high voltage mix in use you will have to remove/break the tab as shown in the instructions.

    Terminals 5 and 6 on the camstat as Shown on the wiring diagram I provided you are for the low voltage/limit wires. 2 and 4 are for the fan switch on the camstat.

    The Honeywell Fan side which is left on the diagram I provided you will use 2 and 4 wires of the cam stat and the limit which is right side of the Honeywell will be used for the 5 and 6 terminals on the that were on the camstat. If low voltage high voltage mix you have to remove/break the tab as shown in the Honeywell diagram.

    I hope this helps.
    jonwilliam's Avatar
    jonwilliam Posts: 31, Reputation: 1
    Junior Member
     
    #8

    Feb 8, 2009, 12:06 PM
    Quote Originally Posted by hvac1000 View Post
    The reason I left this up to you was the wiring is VERY critical if you have a mix of 24 volt and 120 volt wiring in use on your furnace. I have no idea what you have but if you do have a low and high voltage mix in use you will have to remove/break the tab as shown in the instructions.

    Terminals 5 and 6 on the camstat as Shown on the wiring diagram I provided you are for the low voltage/limit wires. 2 and 4 are for the fan switch on the camstat.

    The Honeywell Fan side which is left on the diagram I provided you will use 2 and 4 wires of the cam stat and the limit which is right side of the Honeywell will be used for the 5 and 6 terminals on the that were on the camstat. If low voltage high voltage mix you have to remove/break the tab as shown in the Honeywell diagram.

    I hope this helps.
    HVAC 1000
    Thanks a lot for your explanation yes I have got it now thanks again and have a great day
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #9

    Feb 8, 2009, 02:12 PM
    Good deal you got it working.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

New Honeywell 7-day programmable t-stat ? [ 1 Answers ]

I installed a new Honeywell 7-day programmable t-stat today on my heat pump. It seemed to work fine all day but this evening I smelled a creosote Type smell in the house and attick where the unit is located. I checked the attick for signs of fire, smoak etc but did not locate Or see anything...

Replacing honeywell stat to an other honeywell stat [ 19 Answers ]

I'm switching my old stat to a new one that lets me enter a program. I have an electric central air furnace and a thermopump outside that provides heat and AC. I'm going from a honeywell CT3600 or so (looks the same as in the manual for that one but without the program buttons) to a RTH8500....

Honeywell t-stat [ 2 Answers ]

I have a problem. I am NOT an electrician nor do I want to be one. I have been shocked more times in my life than I can count. I just remodeled my bathroom and put in a new gfci and a hot tub and new light fixtures. I thought I would get brave and replace all of the t-stats in my house with new...

Honeywell stat to braeburn [ 1 Answers ]

I have a honeywell stat t8734c1432. I replaced it with a braeburn 5000. I have a staights cool outside condenser and a gas furnace in the attic. I have no heat after changing the stats. The honeywell is a 4 wire stat with a jumper between the y terminal and terminal 1. white is to w, red to r,...


View more questions Search